[ AS Hardware ] Trigger two output with one event - 20170628
Posted: June 28th, 2017, 5:45 pm
Question:
How to trigger two output at the same time with only one event? Two output should last for different time.
Patch / Procedure:
1. Connect Output 1 to not only Door Lock but also Input 1.
NC <---> In01
COM <---> GND
2. Go to the Web Interface of the Controller, select Input Configuration and follow the settings in the screenshot.
Set Input 01 as NC/Normal Input/Latch Enable.
3. Go to Output Configuration and follow the settings in the screenshot.
Set Output 2 Pulse for 2 Sec after triggered by Input 01.
With the configuration above, Output 1 will follow the lock reset time in ASManager and Output 2 will follow the rule set in controller, yet Output 2 will also be triggered when Output 1 is triggered.
Reference:
[ UVS - 201704245002 ] ASManager V4350, HID Cards not recognized, No live view for Ch1 and Ch2, trigger alarm
How to trigger two output at the same time with only one event? Two output should last for different time.
Patch / Procedure:
1. Connect Output 1 to not only Door Lock but also Input 1.
NC <---> In01
COM <---> GND
2. Go to the Web Interface of the Controller, select Input Configuration and follow the settings in the screenshot.
Set Input 01 as NC/Normal Input/Latch Enable.
3. Go to Output Configuration and follow the settings in the screenshot.
Set Output 2 Pulse for 2 Sec after triggered by Input 01.
With the configuration above, Output 1 will follow the lock reset time in ASManager and Output 2 will follow the rule set in controller, yet Output 2 will also be triggered when Output 1 is triggered.
Reference:
[ UVS - 201704245002 ] ASManager V4350, HID Cards not recognized, No live view for Ch1 and Ch2, trigger alarm