Question:
How to trigger two output at the same time with only one event? Two output should last for different time.
Patch / Procedure:
1. Connect Output 1 to not only Door Lock but also Input 1.
NC <---> In01
COM <---> GND
2. Go to the Web Interface of the Controller, select Input Configuration and follow the settings in the screenshot.
Set Input 01 as NC/Normal Input/Latch Enable.
3. Go to Output Configuration and follow the settings in the screenshot.
Set Output 2 Pulse for 2 Sec after triggered by Input 01.
With the configuration above, Output 1 will follow the lock reset time in ASManager and Output 2 will follow the rule set in controller, yet Output 2 will also be triggered when Output 1 is triggered.