[Technical Notice] How to set PTZ Preset Function with GV-AS200 Controller

Access Control technical notice
alexhon

[Technical Notice] How to set PTZ Preset Function with GV-AS200 Controller

Unread post by alexhon »


Article ID: GV-33-08-07-10
Released Date: 2008/7/10



Applied to
GV-AS200 Controller

Summary
GV-AS200 Controller can work in conjunction with the PTZ camera to perform preset functions on two doors. In this application, one PTZ camera is connected to both outputs of Door B and Door D on the GV-AS200 module. When Door A is opened, the signal of Wiegand A will be transmitted to Wiegand B (Door B) and it will trigger the PTZ camera view moving to Door A. When Door C is opened, the signal of Wiegand C will be transmitted to Wiegand D (Door D) and it will trigger the PTZ camera view moving to Door C.

Requirements
4-door modules: GV-AS200-4 or GV-AS200-4E

To Connect a PTZ to GV-AS200 Controller
  1. The work mode of GV-AS200 Controller must be set to One Way Control. By default, the work mode is One Way Control. If the default setting has been changed, use GV-ASKeypad to modify it.
  2. Connect the card reader to the Wiegand A inputs. Then connect the D0 and D1 pins of Wiegand A with the two same pins of Wiegand B, as illustrated below.
    Screenshot_1.jpg
    Screenshot_1.jpg (19.64 KiB) Viewed 2861 times
  3. Connect the Door + pin of Door B outputs to the Input 1 pin of PTZ. Then connect the Urgent 1 pin of Door B outputs to the Ground pin of PTZ, as illustrated below. Please note don’t connect any power to the Door B outputs.
    Screenshot_2.jpg
    Screenshot_2.jpg (17.73 KiB) Viewed 2861 times
  4. Set the Door Relay Switch of Door B to NO.
  5. Connect the card reader to the Wiegand C inputs. Then connect the D0 and D1 pins of Wiegand C with the two same pins of Wiegand D, as illustrated below.
    Screenshot_3.jpg
    Screenshot_3.jpg (20.1 KiB) Viewed 2861 times
  6. Connect the Door + pin of Door D outputs to the Input 2 pin of PTZ. Then connect the Urgent 1 pin of Door D outputs to the Ground pin of PTZ, as illustrated below. Please note don’t connect any power to the Door D outputs.
    Screenshot_4.jpg
    Screenshot_4.jpg (17.81 KiB) Viewed 2861 times
  7. Set the Door Relay Switch of Door D to NO.
  8. It is required to allow the accessibility of Door B and Door D even though only Door A and Door C are used for entry and exit.
    Screenshot_5.jpg
    Screenshot_5.jpg (37.05 KiB) Viewed 2861 times